Yahoo Answers is shutting down on 4 May 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

split ac no enough cooling?

I checked these and all are perfect

-New outdoor unit with fresh recharge

-New capacitor 

-Out door unit heat fan is running perfectly ,and there is hot air blowing

-Clean filters in indoor unit, and perfectly clean coils

-Fan blows air nicely without any hisses,

i dont know where else to check ,the compressor is performing good

indoor unit is also looking good

8 Answers

Relevance
  • Rita
    Lv 6
    1 month ago

    the most common reason why your split and window AC is not cooling is because of unclean air filters. ... Dirt in the AC filters block the passage of cool and warm air inside the ducts. It could also make the evaporator coil freeze, thus blocking the passage of cool air from the outlet.

  • 1 month ago

    I had the same issue, got some good results with Canadian Duct Cleaning Company https://semsductcleaning.ca/ 

  • ?
    Lv 4
    1 month ago

    Try taking your coat off.

  • Anonymous
    1 month ago

    Get a manifold gauge and check the pressures, superheat and subcooling when the unit has been running for 15 minutes.  It will lead you to the cause.

  • 1 month ago

    actually it was bent copper pipe.,and my ac doesn't have expansion valve,,thanks everyone

  • 1 month ago

    what is the outdoor temperature?  if it is pushing up toward 50 degrees, there's almost no ac unit that will keep you cool.  {and I'd still look at the expansion valve and whether it is stuck or incompatible with the refrigerant}

  • Anonymous
    1 month ago

    May be it is the expansion valve on the A coil in the attic. Did you get a new unit in the attic?   It could be that if you have a real old expansion valve, it is not compatible with the current freon coolant, and does not cool very efficiently.  You will have to change out the expansion valve, and may be the A coil.

  • y
    Lv 7
    1 month ago

    New outdoor unit with fresh recharge?

    Why would a new unit need anything as far as charging it goes?

    If all is running as you say it is definitely the refrigerate, wrong type, wrong, charge, wrong metering device possible.

    What are the amps the compressor pulling? That might tell you something.